LOGO! - Projects: Exit depending linearly Originating From Entry

Hy,
I need help writing a code to control VAV regulators according to CO2 sensor. I need to control in linearly. Like when the CO2 level is 600ppm the output for the regulator is 0V and when the CO2 level is 1100ppm the output is 10V. I am using LOGO8 controller. 
I am new to LOGO )working with TIA portal regurally) so the answer could be very basic, but i havent found it yet. Could someone help me and point me to the right way (reccomend using a specific point or give me a code examplke from where i could go forward)
Thank You in advance,
Martin Mölder

0 Likes 0 Favourites 0 Followers 0 Comments
Answers(1)

Controlling VAV Regulators with CO2 Sensors using LOGO8

Hi Martin,

Here's how you can control VAV regulators linearly with a CO2 sensor using LOGO8. Since you're familiar with TIA Portal, the LOGO!Soft Comfort environment will feel similar, but simplified.

Approach: Analog Scaling

LOGO8 can scale the analog input (CO2 sensor reading) to an analog output (VAV regulator control signal). This is done using the "Analog Scale" block.

Steps & Example Code (LOGO!Soft Comfort):

  1. Input: Connect your CO2 sensor's analog output (4-20mA or 0-10V) to an Analog Input (AI) on the LOGO8.
  2. Output: Connect the VAV regulator to an Analog Output (AO) on the LOGO8.
  3. Network Configuration:
    • Drag an "Analog Scale" block onto your network.
    • Input: Assign the AI where your CO2 sensor is connected.
    • Input_Min: Set to 600 (representing 600 ppm CO2).
    • Input_Max: Set to 1100 (representing 1100 ppm CO2).
    • Output_Min: Set to 0 (representing 0V output).
    • Output_Max: Set to 10 (representing 10V output).
    • Connect the output of the "Analog Scale" block to the AO connected to your VAV regulator.

Example: The scaled value will be linearly mapped between 0V and 10V based on the CO2 level.

Resources:

This approach offers a simple and effective way to achieve linear control of your VAV regulators based on CO2 sensor readings. Let me know if you have any further questions.

Best regards,

Siemens Self Support