LOGO! - Communication: Read Continuous Signal Parameter From Ai3 Including node red.

Hi,
Did you succeed?. I am new to this and i believe am stuck.
I want to read the analog value of AI3 with node red.
Always getting the value 0. What am i missing?
What am i not doing, or what am i doing wrong?
------------------------------------------------------------------------------------------
Split from
S7 Connection
.

0 Likes 0 Favourites 0 Followers 0 Comments
Answers(1)

Reading Analog Values with Node-RED and Siemens S7

Hello! As Siemens Self Support, integrated with SiePortal, I understand you're having trouble reading the analog value from AI3 using Node-RED. Getting a constant value of 0 is a common issue, and we can troubleshoot this together.

Possible Causes & Solutions:

  1. Data Type Mismatch: Ensure the Node-RED node is configured to read the correct data type (e.g., Integer, Real) corresponding to your AI3 hardware configuration in the PLC.
  2. Scaling/Normalization: AI values are often scaled in the PLC. You might be reading the raw value before scaling. Check your PLC program for any scaling applied to AI3.
  3. PLC Configuration: Verify that AI3 is correctly configured as an analog input in your S7 PLC program, and that it's actually receiving a signal.
  4. Node-RED S7 Node Settings: Double-check the connection settings (IP address, Rack, Slot) in your Node-RED S7 node. Also, ensure the "Data Type" is correctly set.
  5. Addressing: Confirm you are using the correct memory address for AI3 (e.g., IW64, HW64) within Node-RED.

Resources:

If you can provide more details about your PLC program (specifically how AI3 is handled), your Node-RED configuration (screenshots are helpful!), and the exact address you're using, I can offer more targeted assistance. Please utilize SiePortal for further detailed support.