LOGO! - Communication: logo 8 Networking Towards Windows Control Center 7.4

hello sir.
so the big question is what driver should i use to connect to logo 8 ?
i have tried s7 communication protocol suite -> tcp/ip and enter the ip of the logo ( the connection between logo and PC is direct through lan cable) but the status always disconnected.
is there special communication that i have miss ? or there is a download driver for logo8 ?
Best regard

0 Likes 0 Favourites 0 Followers 0 Comments
Answers(29)

Writing to Modbus Input Registers with LOGO!

You are correct to have seen posts stating LOGO! cannot directly write to Modbus Input Registers. LOGO! Modbus TCP/RTU communication is primarily designed for reading from Input/Holding Registers and writing to Holding Registers only.

Why Input Registers are Read-Only for LOGO! writes: The LOGO! Modbus Master function blocks are configured to write to Holding Registers (function code 6). Input Registers (function code 4) are typically read-only for security and data integrity reasons.

Solution: If the Modbus device allows it, you'll need to map the data you want to write to a Holding Register instead. Consult the Modbus device’s documentation to see if register 406000 can be configured to function as a Holding Register, or if there's an alternative Holding Register you can use for the same purpose.

Resources:

If you confirm the target device supports writing to a Holding Register, please provide details about the data type and range, and I can help you configure the LOGO! program accordingly.

0

Creating an HMI Screen for LOGO!

Hi there!

You're on the right track with the LOGO! Soft Comfort Starter Kit. To create a PC-based HMI (Human Machine Interface) for your LOGO! and run it remotely (e.g., via VNC), you'll need LOGO! Soft Comfort – specifically, a version that includes HMI functionality.

The Starter Kit (6ED1057-3BA00-0AA7) typically includes a limited version of LOGO! Soft Comfort which might not support the full HMI editing features. You'll likely need to upgrade to the full version of LOGO! Soft Comfort 8 or newer.

Here's a breakdown & resources:

  • LOGO! Soft Comfort 8 (or newer): This is the software that allows you to design and simulate HMI screens. Learn more here.
  • VNC/Remote Access Software: To access the PC-based HMI remotely, you'll need VNC or similar remote desktop software.

Important Note: Ensure the version of LOGO! Soft Comfort you purchase is compatible with your LOGO! hardware.

As a home enthusiast, purchasing the full version of LOGO! Soft Comfort gives you the flexibility to develop complex HMIs and explore the full potential of your LOGO! system.

For detailed information and to purchase software, please visit the Siemens LOGO! website or contact your local Siemens distributor.

0

Email Setup with Gmail and CMR - CA Certificate Format

Hello Murillo,

Siemens CMR requires the CA certificate to be in .CER format for proper upload and functionality when configuring email services with Gmail.

While Gmail provides certificates in PEM and DER formats, you'll need to convert them to CER. You can use online conversion tools or OpenSSL for this conversion. Here's a basic OpenSSL command example:

openssl x509 -in your_gmail_certificate.pem -out your_gmail_certificate.cer -outform DER

Important Resources:

Please ensure the converted CER file is valid before uploading it to CMR.

If you continue to experience issues, please open a support request via SiePortal, including details of the conversion process and the error message.

Best regards,
Siemens Self Support

0
LOGO! 8 Ethernet Download Issue

LOGO! V7 Ethernet Download Problem - "Can't Access IP"

Hello! Siemens Self Support here, integrated with SiePortal.

The "Can't access IP" message, despite a successful ping, usually indicates a firewall or port blocking issue. Here's a breakdown:

  • Firewall: Your Windows Firewall (or other firewall software) might be blocking the communication on specific ports required for LOGO!Soft Comfort to download the program.
  • Port Blocking: LOGO!Soft Comfort uses specific ports (typically UDP 502) for Ethernet communication. Ensure these ports aren't blocked.
  • LOGO! Web Server: Ensure the LOGO! web server is enabled.

Troubleshooting Steps:

  1. Disable Firewall Temporarily: As a test, temporarily disable your Windows Firewall to see if the download succeeds. Important: Re-enable it immediately after testing!
  2. Check LOGO! Settings: Verify that the LOGO! is configured for Ethernet communication and that the IP address is correctly set.
  3. LOGO!Soft Comfort Settings: Confirm that LOGO!Soft Comfort is configured to use the correct Ethernet interface.
  4. Port Configuration: If you have a router, ensure port forwarding is not interfering with communication.

For detailed troubleshooting and FAQs, please refer to these resources on SiePortal:

If the issue persists, please provide your LOGO!Soft Comfort version and operating system for further assistance.

0

Understanding LOGO! 8.FS4 Modbus TCP Control

Hello! Siemens Self Support here, integrated with SiePortal. You're right to identify the client/server roles. The LOGO! 8.FS4, when using Modbus TCP, typically operates as a Modbus Server, not a client.

However, controlling coils via Modbus TCP requires writing to specific registers. The LOGO! 8's Modbus interface provides access to its memory, including coils (outputs). You need a Modbus TCP Client (like your Arduino or QModMaster) to send write requests to these coil registers.

Key Considerations:

  • Configuration: Ensure the LOGO! 8 is configured as a Modbus TCP Server within its settings.
  • Address Mapping: Carefully check the LOGO! 8's Modbus register map to determine the correct addresses for the coils you want to control. This is crucial for correct operation.
  • Data Types: Use the correct Modbus function code (typically 06 for writing to a single coil) and data type.

Resources:

If you continue to face issues, please provide details on your LOGO! 8 configuration and the specific Modbus commands you're using, and I’ll assist further. You can also find more detailed information and support through the SiePortal.

0

CMR 2040 Firmware Issue - Placeholders Not Resolving

Dear User,

It appears you're experiencing an issue with placeholder resolution in your CMR 2040's firmware, specifically with text messages containing multiple signal placeholders. The first placeholder resolves correctly, but subsequent ones display as "!xxx!".

Here are potential causes and troubleshooting steps:

  • Signal Configuration: Verify that all four signals are correctly configured within the CMR 2040. Ensure they have valid data types and are actively updating.
  • Placeholder Syntax: Double-check the placeholder syntax in your message template. Ensure consistency and correct signal referencing.
  • Firmware Bug: There may be a bug in the current firmware version related to placeholder handling with multiple signals.

Recommended Actions:

  1. Review SiePortal: Search SiePortal for known issues related to CMR 2040 firmware and placeholder resolution.
  2. Update Firmware: If a newer firmware version is available, updating might resolve the bug.
  3. Simplify Test: Create a simple test message with just the problematic placeholders to isolate the issue.
  4. Siemens Support: If the problem persists, please create a support request through SiePortal, providing details of your configuration, firmware version, and the message template.

Sincerely,
Siemens Self Support

0
AWS IoT Connection Issue - Siemens Self Support

AWS IoT Connection Troubleshooting

Hello Wilson,

The "Cannot connect to AWS IoT" error, despite valid credentials, often points to network connectivity or security group configurations. Here's a breakdown of potential solutions:

  1. Network Connectivity: Double-check your internet connection stability. A seemingly active connection can have intermittent issues.
  2. Firewall/Proxy: Ensure your firewall or proxy settings aren't blocking outbound connections to AWS IoT endpoints.
  3. Security Groups: Verify your AWS Security Groups allow inbound traffic on port 443 (HTTPS) from your IP address.
  4. Cloud Access Setting: While "secured" is the intended setting, temporarily switching to "unsecured" (for testing ONLY) can help isolate if the security settings are causing the issue. Remember to revert to "secured" after testing!

For detailed guidance, please refer to the following SiePortal resources:

If the problem persists, please provide your region and the exact error message for further assistance.

Best regards,
Siemens Self Support

0

Sending LOGO! PLC Data to AWS & Webpage Creation

Congratulations on successfully registering with AWS IoT! You've completed a significant step. Creating the webpage in AWS to visualize your LOGO! PLC data requires using AWS services like IoT Core, Lambda, and potentially API Gateway with a frontend hosted on S3 or a similar service.

Here's a breakdown and helpful resources:

  1. AWS IoT Core Rule: Configure a rule to forward your LOGO! PLC data to an AWS Lambda function.
  2. AWS Lambda Function: This function processes the data and stores it in a database (like DynamoDB) or sends it to other AWS services.
  3. API Gateway (Optional): Create an API endpoint to access the data from your Lambda function.
  4. Frontend Webpage: Develop a webpage (HTML, CSS, JavaScript) to retrieve data from the API Gateway (or directly from DynamoDB if you prefer) and display it. Host this webpage on AWS S3 or another suitable hosting service.

Tutorials & Examples:

SiePortal Search: For more specific examples related to LOGO! and AWS, try searching SiePortal using keywords like "LOGO! AWS webpage" or "LOGO! AWS data visualization".

0

SMS Control of Logo! 8 I/O Status via CMR 2040

You're looking to trigger a specific I/O status report from your Logo! 8 using a custom SMS alias sent via the CMR 2040. This is achievable, but requires some configuration and understanding of the Logo! 8's network capabilities.

Directly accessing the "backend" to modify Logo! 8 behavior isn't generally supported or recommended. Instead, leverage the Logo!'s network functions.

Recommended Approach:

  1. Network Output Mapping: In your Logo! 8 program, map the status of the specific I/O you wish to monitor (e.g., M1) to network outputs (e.g., NW1).
  2. CMR 2040 Configuration: Configure the CMR 2040 to send an SMS command (your alias) that triggers a request to the Logo! 8 over the network.
  3. Logo! 8 Network Request Handling: Create a network input block in your Logo! 8 program. When this input is activated (by the CMR 2040's request), build an SMS message string containing the current status of the mapped network outputs (NW1, NW2, etc.).
  4. SMS Transmission: Use the CMR 2040 to read the response from Logo! 8 network output and forward that status as an SMS.

Important Considerations:

  • The CMR 2040 must be able to communicate with the Logo! 8 over the network (Ethernet or WiFi).
  • You'll need to define a clear communication protocol between the CMR 2040 and the Logo! 8 (e.g., a specific network command to request the status).
  • The SMS message length is limited, so keep the status report concise.

Resources:

This method avoids sending the entire Logo! 8 configuration and provides a user-friendly, targeted status report.

0

Troubleshooting LOGO!8 Remote Access - Despite Ping & Network View

Hello, as Siemens Self Support integrated with SiePortal, I understand you're facing connection issues with your LOGO!8 despite successful ping and visibility in Soft Comfort's Network View, similar to the case referenced here.

Since ping is successful and the LOGO! is visible in Soft Comfort, the issue is likely with the communication protocol or firewall settings, even though you have basic connectivity.

Recommended Steps:

  • Firewall Check: Temporarily disable the Windows Firewall on your PC to see if it's blocking Soft Comfort's communication with the LOGO!. If this resolves the issue, configure the firewall to allow Soft Comfort access.
  • Soft Comfort Version: Ensure you are using the latest version of Soft Comfort. Older versions might have compatibility issues.
  • LOGO! Firmware: Check and update the LOGO!8 firmware to the latest version via Soft Comfort (if possible, even with limited access).
  • Ethernet Cable & Port: Although seemingly basic, try a different Ethernet cable and port on both the PC and LOGO!.
  • Soft Comfort Configuration: Double-check the communication settings *within* Soft Comfort itself. Ensure the correct protocol (typically UDP) is selected.

If these steps don’t resolve the problem, please provide the following information for further assistance:

  • Soft Comfort version
  • LOGO!8 firmware version
  • Windows Operating System version
  • Screenshots of the Soft Comfort communication settings.

You can find further resources and FAQs on the Siemens Industry Online Support.

0

LOGO! PLC & Wonderware System Platform Compatibility

Based on your query and the provided documentation, direct communication between LOGO! PLCs and your Aveva Wonderware System Platform via the SIDirect DAServer is not directly supported.

The SIDirect DAServer specifically supports S7-200/300/400/1200 controllers using TCP/IP communication. While LOGO! PLCs can communicate over TCP/IP, they don't natively utilize the S7 protocol expected by the SIDirect DAServer.

Options to consider:

  • S7 Controller: Using S7 PLCs (S7-1200/1500) ensures compatibility with your existing Wonderware setup.
  • Third-Party Gateway: Explore third-party gateways that can translate LOGO! communication to a protocol supported by Wonderware.
  • LOGO! 8 with Modbus TCP: LOGO! 8 supports Modbus TCP, which might be compatible with Wonderware through a suitable Modbus driver. See Siemens FAQ on LOGO! 8 and Modbus TCP.

We recommend verifying Modbus TCP compatibility with Wonderware or contacting Wonderware support for clarification before implementing that solution.

0

LOGO! 8 and Web Access - 6ED1052-1MD00-0BA8

We understand your frustration regarding the web access limitations with the LOGO! 8 6ED1052-1MD00-0BA8. You are correct; not all 0BA8 variants support web server functionality. We apologize for any misleading information you may have encountered.

Unfortunately, the 6ED1052-1MD00-0BA8 does not support direct web access for visualization or parameter changes. It lacks the necessary firmware for the integrated web server.

However, you still have options for remote monitoring and control:

  • LOGO! 8 App (Android): The LOGO! 8 App allows you to monitor inputs/outputs and program variables. Basic control of process variables (like room temperature) is possible through the app, depending on your program logic.
  • Remote Access via VPN: Establish a VPN connection to your network to access the LOGO! 8 via LOGO!Soft Comfort software on a computer.
  • Third-party IoT Solutions: Integrate the LOGO! 8 with a third-party IoT platform (e.g., using Modbus TCP) that provides web-based dashboards and remote control.

While a direct "teleservice" style web interface isn't available, the LOGO! 8 App provides a viable solution for monitoring and basic control of your heat pump. We will forward your feedback regarding clearer product labeling to the relevant teams.

For detailed information, please refer to the LOGO! 8 FAQ and Compatibility of LOGO! 8 with Web Access in SiePortal.

0

Reading Modbus Data Beyond Network Analog Input Limits in LOGO!

You're right to identify the 32 Network Analog Input limit in LOGO!. While using Modbus to VW transfer and then Network Analog Inputs is a common approach, it quickly becomes restrictive. Here are alternative ways to access your Modbus data within the LOGO! program:

  • Use VW Memory Directly: Instead of relying solely on Network Analog Inputs, directly read the values stored in the VW memory within your LOGO! program logic (e.g., using Compare blocks, mathematical operations). This bypasses the 32-input limit.
  • Flags & Math Blocks: Transfer Modbus data to VW areas, then use flags and mathematical blocks to process and utilize the data as needed within your program.
  • LOGO! 8.3 & Higher - Extended Modbus Support: LOGO! 8.3 and later versions offer enhanced Modbus functionality, including direct access to Modbus registers within program blocks. See Siemens Support article for more details.

Recommendation: Upgrade to LOGO! 8.3 or higher to leverage the more flexible Modbus integration features. If an upgrade isn't feasible, focus on directly utilizing the VW memory where the Modbus data is stored within your program logic.

0

LOGO! 230RCE Connection Issue - "Unable to access remote device"

Based on your description, the issue likely stems from a communication mismatch despite successful pinging. Here's a breakdown of potential causes and solutions:

Possible Causes & Solutions:

  • LOGO! Software Version: Ensure you're using a LOGO!Soft Comfort version compatible with the LOGO! 230RCE (0BA8). Older versions may have connectivity issues. Check Compatibility Here
  • Communication Settings: Double-check the communication settings within LOGO!Soft Comfort (Tools -> Options -> Communication). Verify the correct communication channel (Ethernet) and port (typically UDP 52001) are selected.
  • IP Address Conflicts: Although you can ping, a temporary IP address conflict on the network *could* disrupt the LOGO!Soft Comfort connection. Try assigning static IP addresses to both your PC and LOGO! outside of your DHCP range to eliminate this possibility.
  • Firewall/Antivirus: While you disabled Windows Firewall, ensure no other firewall or antivirus software on either PC is blocking LOGO!Soft Comfort's communication. Temporarily disabling these (with caution) can help diagnose.
  • Network Cable/Port: Test with a known good network cable and a different port on your router/switch.

Wireshark Analysis (If Needed):

If the above steps don't resolve the issue, Wireshark can be helpful. Look for:

  • Communication attempts from LOGO!Soft Comfort to the LOGO!'s IP address on UDP port 52001.
  • Any dropped packets or retransmissions.

Further Support:

If you continue to experience problems, please open a support request via SiePortal, including details of your LOGO!Soft Comfort version, network configuration, and any Wireshark captures.

0

Troubleshooting Modbus Coil Write with LOGO! 8.3

Hello, thanks for reaching out to Siemens Self Support!

It's common to encounter issues when first implementing Modbus with LOGO! 8.3. Here's a breakdown of potential causes and troubleshooting steps, given your successful ping test but lack of coil control:

Key Considerations:

  • Data Type Mismatch: Ensure you're using the correct data type for the coil write. Coils are typically represented as single bits (0 or 1). The Network Output block in LOGO! expects a Boolean value (ON/OFF).
  • Modbus Function Code: LOGO! 8.3 typically uses Modbus function code 0x05 (Write Single Coil) for writing to coils. While the Network Output block handles the communication, verify the target device is configured to respond to this function code.
  • Addressing: Double-check your coil address. Modbus addressing often starts at 0, but some devices use 1. Also, confirm if the address is a coil *number* or a register address that corresponds to a coil.
  • Network Output Block Configuration: In the LOGO!Soft Comfort software, carefully verify the following in the Network Output block's settings:
    • Connection Settings: Correct IP address and port (typically 502).
    • Data Format: Set appropriately for a single coil write.
  • Target Device Configuration: Confirm the Modbus device is listening on the correct port and IP address. Also, check its coil configuration to ensure the coil is writable.

Recommendations:

  1. Simplify the Test: Start with the simplest possible test: a constant HIGH signal into the Network Output block connected to coil address 0 (or 1, depending on your device). This isolates the issue.
  2. Packet Capture: Use a tool like Wireshark to capture the Modbus traffic between the LOGO! and the target device. This will show you the exact Modbus commands being sent and the device’s responses (or lack thereof). Wireshark Download
  3. Check LOGO! Diagnostics: Beyond the ping test, use the LOGO!'s built-in Modbus diagnostics to monitor communication status and any errors.
  4. Review SiePortal Knowledge Base: Search SiePortal for specific error messages or keywords related to "LOGO! Modbus coil write" for similar cases. SiePortal Link

The video you referenced can be a good starting point, but ensure all settings align with your specific device's Modbus implementation. If you continue to have issues, providing details of your target device and the exact settings you’re using in LOGO!Soft Comfort will help me assist further.

0
LOGO 8 Access via Router

Accessing LOGO 8 via Residential Router

Hello Kevin, welcome to the LOGO 8 world! It's great you're starting with a test program. The issue you're facing – inability to access the LOGO 8 when connected through a router – is common. Here's a breakdown of potential causes and solutions:

Troubleshooting Steps

  1. IP Address Conflict: Your router likely assigns IP addresses dynamically. The IP address the LOGO 8 had when connected directly to your laptop is probably different now. Check your router's DHCP client list to find the IP address assigned to the LOGO 8.
  2. Subnet Mask: Ensure the LOGO 8's subnet mask matches your router's subnet mask. Usually, this is 255.255.255.0 for home networks.
  3. Router Firewall: Your router’s firewall might be blocking access to the LOGO 8. Temporarily disable the firewall (for testing *only*!) to see if that resolves the issue. If so, you'll need to create a firewall rule to allow traffic to the LOGO 8's IP address and port 80 (HTTP) or 443 (HTTPS, if enabled).
  4. LOGO 8 Network Configuration: Verify the LOGO 8's IP address, subnet mask, and gateway settings within LOGO!Soft Comfort. Ensure the gateway is set to your router's IP address.
  5. Ping Test: From your laptop, try pinging the LOGO 8's IP address. If the ping fails, it confirms a network connectivity issue.

Resources

For detailed guidance, please refer to the following resources on SiePortal:

Regarding your Swimming Pool Controller project, the LOGO Soft Web Editor will eventually simplify this process, but getting basic network connectivity working first is crucial.

Good luck, and feel free to post updates or further questions!

0

Data Transfer Limitation in Master/Slave Mode with 0BA8

You are encountering a known limitation in the 0BA8 PLC when configured in Master/Slave mode. The Master/Slave communication protocol restricts data transfer to 32 data points (inputs/outputs) per connection.

As you've observed, using Master/Master mode with multiple connections bypasses this limitation, allowing access to all I/O.

Unfortunately, there is no direct way to bypass the 32 data transfer limit within the standard Master/Slave configuration. The limitation is inherent to the protocol implementation.

Workarounds/Alternatives:

  • Switch to Master/Master mode: This is the recommended solution if your application allows.
  • Reduce Data Transfers: Optimize your data exchange to transfer only essential I/O points.
  • Multiple Master/Slave Connections (Not Recommended): While technically possible with multiple connections, it significantly increases configuration complexity and is generally not recommended due to potential communication overhead and synchronization issues.

For detailed information on Master/Slave vs. Master/Master configuration, please refer to the following SiePortal documentation:

SIMATIC PCS 7 - Master/Master and Master/Slave Communication
0

LOGO V8.3 & Modbus TCP with Arduino - Communication Issue

Hello, we understand you're experiencing issues with Modbus TCP communication between your LOGO 8.3 and Arduino after upgrading from V8.FS4.

Here are some potential solutions/ideas:

  • Firmware Compatibility: Ensure your Arduino's Modbus library is compatible with the LOGO 8.3's Modbus TCP implementation.
  • Modbus Address Mapping: Double-check your Modbus address mapping in both the LOGO 8.3 and Arduino code. A mismatch could cause read failures.
  • Network Configuration: Verify the network settings (IP addresses, subnet masks, gateway) are correctly configured on both devices and that they are on the same network.
  • LOGO 8.3 Configuration: Re-confirm "Allow Modbus Access" is enabled and that the Modbus TCP server settings (port, etc.) are correctly configured within the LOGO 8.3 software.
  • Firewall: Temporarily disable any firewalls on your network or on the Arduino to test if they are interfering with the communication.

For more detailed troubleshooting and specific configuration guidance, please refer to the following resources in SiePortal:

If the problem persists, please provide your LOGO 8.3 program (relevant parts) and Arduino code (Modbus section) for further assistance.

0

LOGO 8FS4 - Password Prompt & Functionality Issues

It appears you're encountering issues with a password prompt and subsequent operational problems after program modifications and downloads to your LOGO 8FS4 using LOGO!Soft Comfort V8.3.

Here's a breakdown of potential causes and troubleshooting steps:

  • Password Protection: The LOGO 8 can enable password protection. It's possible it was unintentionally activated during a previous download or program change.
  • Communication Issues: While the initial connection was established, intermittent communication problems can corrupt data during downloads, leading to unexpected behavior.
  • Firmware/Software Compatibility: Ensure your LOGO!Soft Comfort V8.3 is fully compatible with the LOGO 8FS4 firmware.
  • Corrupted Program: The program itself might have become corrupted during the download process.

Recommended Actions:

  1. Default Password: Try the default password "0000" (four zeros) if "LOGO" doesn't work.
  2. Restart Everything: Power cycle the LOGO 8FS4 and your computer.
  3. Check Communication: Verify the USB connection and ensure no other programs are interfering with communication.
  4. Re-download Original Program: Attempt to download the original program *again*, carefully monitoring for errors.
  5. Factory Reset (Last Resort): As a final step, consider a factory reset of the LOGO 8FS4 (refer to the LOGO 8 manual for instructions). Warning: This will erase the current program!

For more detailed troubleshooting and FAQs, please refer to the Siemens Support articles and documentation on SiePortal:

If the problem persists, please gather details about the specific error messages, program size, and any changes made before the issue arose, and create a support request on SiePortal for further assistance.

0

Displaying LOGO! 0BA2 TDE Data on a Smartphone (No Internet)

You're looking for a local, wireless display of your LOGO! 0BA2 TDE data on a smartphone within a 20-meter range, without internet access. Your router/WiFi approach is viable, but here's a breakdown and alternatives:

Your Router/WiFi Approach:

This is a good starting point. You’ll need a router capable of creating a local WiFi network and a method to get the LOGO! data onto that network. Unfortunately, the LOGO! 0BA2 doesn't natively support WiFi. You would need an intermediary device.

Alternative Approaches & Considerations:

  • LOGO! 8 with WiFi Module: Consider upgrading to a LOGO! 8 and adding the WiFi Communication Module (6ED1055-1HB00-0BA6). This provides native WiFi connectivity for direct smartphone access via a dedicated app.
  • Serial Communication & Bluetooth: Connect to the LOGO! via serial (RS232/RS485) and use a Bluetooth adapter connected to a small computer (Raspberry Pi Zero W is ideal). The Pi can then serve the data to the smartphone via Bluetooth.
  • OPC UA & Local WiFi: A more complex solution, but possible. Implement an OPC UA server on a Raspberry Pi and connect to the LOGO! using a suitable protocol (Modbus TCP via Ethernet if you add an Ethernet module to the LOGO!). The Pi then broadcasts data via a local WiFi network.

Tips for your Router Approach (if sticking with LOGO! 0BA2):

  • Data Conversion: The LOGO! TDE data needs to be converted to a format understandable by the smartphone. A small intermediary device or custom programming is required.
  • Router Configuration: Configure the router for a closed, password-protected local network.
  • App Development: You’ll likely need a custom Android app (or find a generic Modbus TCP/Serial client app) to read and display the data sent by the intermediary device on the WiFi network.

SiePortal Resources: Explore the LOGO! 8 FAQ and search for "remote access" or "mobile visualization" for more ideas.