I'd like to use ET200SP in the new project, normally we are using ET200S.
When i made configuration in the selection tools, i've got message about the analog output module: AQ 4xU/I ST
(6ES7135-6HD00-0BA1)
"Note the derating of the analog output modules at ambient temperature of more than 30C with horizontal mounting position or 20C with vertical mounitng position"
Details: "Not all channels of the analog output module can be used at an ambient temperature of more than 30C or 20C, The use depends of the load of the connected actuators and the ambient temperature"
On the site below, page 24, there are derating trend
https://cache.industry.siemens.com/dl/files/612/59753612/att_83040/v1/et200sp_aq_4xu_i_st_manual_en-US_en-US.pdf
My question is, what heppedns when temperature will be higher than 30C? -
The module will shut down, i will get just the error? - I cannot find this information.
I want use the analog outputs to controll Samson positioners, (positioner input = 200Ohm). The main CPU is CPU315-2 PN/DP. The ambient temp, about 20-35C (depend of the weather)
Instead of 4xU/i ST module I can use 2xU.I HF module, but than the ET200SP is much more expensive than ET200S.
Thanks
Robert
Dear Robert,
Regarding your question about the AQ 4xU/I ST (6ES7135-6HD00-0BA1) module's behavior at temperatures exceeding 30°C, the module will not necessarily shut down. Instead, the available output current per channel is reduced due to derating. You will likely not get a hard error, but performance will be limited.
As detailed in the manual (see page 24), the permissible current depends on the ambient temperature and the load (actuator resistance). With a 200 Ohm load (Samson positioners), and temperatures between 20-35°C, you'll need to consult the derating graphs to determine how many channels can operate at their full specification.
For your application (200 Ohm load, 20-35°C ambient): You may be able to use all 4 channels at lower temperatures, but fewer channels as the temperature approaches 35°C. If you need to guarantee full performance of all 4 channels consistently, the AQ 2xU/I HF module might be necessary, despite the higher cost.
The CPU 315-2 PN/DP does not directly influence the module's derating characteristics; it's purely a function of the module and ambient temperature/load.
Sincerely,
Siemens Self Support