Hello All,
I use a CPU 1513-1 PN CPU equipped on the same backplane with a AI 8XU/I HS analog input card (531-7NF10-0AB0). I only have one TP1200 and 3 S120 VFDs on this network. No isochronous mode has been set up (as I know of)
I have an unstable signal on the input due to the previous equipment in the acquisition chain. Nothing to do on that side.
I found out the "Smoothing" function in the hardware configuration of the card. I set it to Strong (k=32).
I would like to quantify this time window. In the manual the following formula is used :
"Smoothing time = number of module cycles (k) x cycle time of the module." (
Manual, 12/2016, A5E03484886-AE)
I am unable to find out what is the "cycle time of the module"
Is it the " Basic execution time of the module (all channel released) => 62.5 us
Or the "Isochronous mode Bus cycle time (TDP), min" => 250us
Or the "CPU cycle time" like for oversampling for example? => variable depending on OB1 or 10ms if OB35 used at 10ms
Thank you in advance for your answers.
Regards
Victor
Dear Victor,
You are correct to question the "cycle time of the module" for the smoothing function calculation. For the AI 8xU/I HS module, use the Basic execution time of the module (all channels released) which is 62.5 µs. This value represents the time the module needs for one complete scan of all channels, and is the correct basis for the smoothing time calculation.
Here's why the other options are not suitable:
Therefore, with your setting of k=32 (Strong smoothing), the Smoothing Time = 32 * 62.5 µs = 2000 µs or 2ms.
For further details, refer to the A5E03484886-AE manual section on Analog Input Modules and the Smoothing Function Siemens Industry Online Support.
Sincerely,
Siemens Self Support
Our flexible community website is a platform that allows users to connect, share information, and collaborate on various topics of interest. The website offers a range of features such as discussion forums, messaging, user profiles, event calendars, and more. Users can customize their experience by creating and joining different groups or communities based on their interests or location. The website is designed to be user-friendly and adaptable to the needs and preferences of our diverse user base. Whether you are looking to network professionally, share hobbies and interests, or simply connect with like-minded individuals, our flexible community website has something for everyone. Join us today and become a part of our thriving online community!