HI ALL
HOW CAN I MAKE COMMUNICATION BETWEEN S5-115U AND ALSTOM PLC
Hello, I'm Siemens Self Support, integrated with SiePortal. You're encountering an issue downloading OB31 to your S5-115U 944 CPU, resulting in a "cannot transfer system block" error and preventing RUN mode. This typically indicates a hardware or configuration problem.
Here's a breakdown of potential causes and troubleshooting steps:
Important Resources:
If the battery replacement and basic checks don’t resolve the issue, consider contacting Siemens Technical Support via SiePortal Request Support for further assistance. Please have your CPU's serial number ready.
Based on the information provided, connecting a Siemens S5 PLC with an IM308C and a Schneider Electric TSX P57 4634M Modbus TCP/IP PLC using the Anybus AB7634 gateway is likely possible, but requires careful configuration.
The key is the Anybus AB7634's PROFIBUS slave functionality (DPV1, Class 1 & 2) and its Modbus TCP/IP server capabilities. The IM308C supports PROFIBUS DP, and the gateway will act as a bridge. The TSX P57 will communicate via Modbus TCP/IP to the Anybus gateway.
However, compatibility with the IM308C is not guaranteed as the IM308C is an older component. You should verify:
Review the Anybus AB7634 manual here for detailed configuration instructions and PROFIBUS compatibility notes. Also, consult the SiePortal knowledge base for specific S5/IM308C PROFIBUS configurations.
Recommendation: Conduct thorough testing in a non-production environment before deploying this solution.
Based on your detailed description, the intermittent bus faults and process image update errors when using the 6ES5 318-8MB13 suggest a compatibility or signal integrity issue within the Profibus network, specifically affecting the communication with output cards.
Here's a breakdown of potential causes and suggestions:
Regarding ET200 Replacement:
The ET200M is generally a reliable choice, but it is a significant wiring change. Your concern about downtime is valid. The ET 200S is a more direct replacement for the ET200U in terms of wiring. It maintains the same terminal types and backplane compatibility.
Important Considerations:
Given the history of the original rack's resilience, the ET200S seems the most viable option to minimize rewiring and maintain reliability. However, thoroughly investigate the Profibus network before committing to a hardware upgrade.
Hello James, welcome to Siemens Self Support! It sounds like you're facing an intermittent STOP issue with your S5 PLC controlling mixing machines. Interpreting the I (Input) and B (Bit) stacks is crucial for diagnosing such problems.
Here's how to get started. These resources are available via SiePortal:
Specifically, look for patterns in the I/B stack when the PLC goes into STOP. The I-stack will show which input triggered the current block, and the B-stack shows the current chain of blocks. Intermittent issues can be challenging, but consistent analysis during each STOP event will help pinpoint the source.
If you're still facing difficulties after reviewing these materials, please provide the specific error code displayed when the PLC stops. This will help me offer more targeted assistance.
Best regards,
Siemens Self Support
Dear Chema,
The w32_511 driver, enabling communication between a PC and a STEP 5 PLC using functions like db_read, dx_read, db_write, and dx_write, is typically found within the STEP 5 V7.x software package.
You can download the STEP 5 V7.x software, including the w32_511 driver, from the Siemens Industry Online Support. You will need a valid Siemens account and possibly a license or service agreement to access the download.
Alternatively, if you already have STEP 5 installed, check your installation directory for the driver files. Refer to the STEP 5 documentation for specific installation and usage instructions. STEP 5 Documentation
For further assistance, please consult the SiePortal knowledge base or contact Siemens support directly.
Sincerely,
Siemens Self Support
Dear Rusli,
Yes, you typically need to call FB7 twice when handling fetching requests with only the FB7 block (P_RCV_RK).
First Call: To receive the fetch request from the partner CPU.
Second Call: To provide the requested data back to the partner CPU.
This two-step process is fundamental to how FB7 operates within S5-S7 communication. For more detailed information, please refer to the SiePortal documentation on S7 communication and FB7 specifically:
S5-S7 PtP Communication (Original Thread)
Sincerely,
Siemens Self Support
Thank you for reaching out to Siemens Self Support. Based on the image provided (though visibility is limited without the actual image content), conversion errors from S5 to S7 are common and often require detailed investigation.
Here's a recommended approach, leveraging SiePortal resources:
Please provide the *exact* error messages from the log for more specific guidance. Attaching the error log file directly would be ideal.
Hello Norm,
The S5 programming software (STEP 5) is an older product and is no longer officially available for download from Siemens directly. However, here's information regarding access:
As a first step, please check this FAQ on Siemens Support for information on obtaining legacy software. You may need a valid maintenance agreement or special arrangement.
You are correct that third-party suppliers may offer STEP 5. However, Siemens does not endorse or support software obtained from unofficial sources. Please exercise caution and ensure the supplier is reputable to avoid potential issues with licensing or software integrity.
Disclaimer: Using software from unverified sources can pose security risks. Siemens recommends exploring official support channels first.
For further assistance, please visit SiePortal or contact Siemens Industry Support directly.
Sincerely,
Siemens Self Support
Hello, as Siemens Self Support, integrated with SiePortal, I can assist you with migrating your project.
Direct Function Block (FB) compatibility between IP246/IP281 and FM453/FM450 is limited. A direct migration is often not possible without adjustments.
For detailed guidance and specific FB recommendations, please use SiePortal's search function with keywords like "FM453 migration," "FM450 migration," and relevant FB names. You can also raise a support request through Siemens Support.
Yes, the correct replacement battery for most Siemens SIMATIC S5 PLCs is typically an LS14250 3.6V Lithium battery. This is a common and reliable choice.
Important: Replacing the battery while the processor is in RUN mode is not recommended. While some users report success, it carries a significant risk of losing the PLC program and/or damaging the memory.
Best Practice: To avoid program loss, always follow these steps:
For detailed instructions and safety information, please refer to the Siemens Industry Support article:
How do you replace the battery in a SIMATIC S5 PLC?You can also find further information within the SiePortal knowledge base by searching for "S5 PLC battery replacement".
Dear Sulistiyo Heri,
Yes, you can generally replace the 6ES5 470-8MB12 with the 6ES5 470-8MC12. Both cards offer similar functionality for analog output.
However, there might be minor differences in hardware specifications (e.g., isolation voltage). Therefore, a review of the manuals is crucial. You can find the manuals on SiePortal:
Regarding programming and addressing: In most cases, the address remains the same. However, always verify this in your PLC program (STEP 5) and compare the parameter settings in both cards after the replacement. Check for any differences in scaling or offset settings.
For checking the lifetime/discontinuity of S5 PLC modules (including analog modules), please refer to this FAQ on Siemens Support. It details diagnostic tools and procedures.
Sincerely,
Siemens Self Support
You've correctly identified a potential issue with multiple assignments of the same memory bit within a block. In TIA Portal (and generally in PLC programming), when multiple networks attempt to write to the same memory bit, the last network evaluated will determine the final state of that bit.
In your example:
A M25.0 = M200.7A M25.1 = M200.7M200.7 will reflect the state of M25.1. If M25.1 is "1", M200.7 will be "1". If M25.1 is "0", M200.7 will be "0". Network 1's assignment is overwritten by Network 2.
Important Considerations:
For more detailed information on data consistency and avoiding such issues, please refer to the Siemens documentation:
Data consistency in STEP 7 (TIA Portal)Hello!
Yes, you typically do need a standard Function Block (FB) for communication even when using the PG/SI1 port with a CPU95 and OP15A. The FB handles the data exchange protocol.
Specifically, you'll likely need to use FB260 (OP15A Communication) or a similar FB designed for operator panel communication on S5/S7-95 PLCs.
Given the age of the PLC, refer to the original documentation for both the CPU95 and OP15A. You can find relevant manuals and support articles on the Siemens Industry Online Support portal:
Siemens Industry Online Support
Search for "CPU95 OP15A communication" or "FB260" on SiePortal. This will provide details on configuration and FB usage.
Remember to configure the correct communication parameters (baud rate, parity, etc.) in both the PLC and the OP15A.
Dear Vibha,
Upgrading a Step 5 system without a program backup and lacking communication ports presents challenges. Here's a breakdown of potential solutions and resources:
Without a visible communication port, retrieving the program is difficult. Consider these options:
The S5-110 user manual is available on the SiePortal. Please use the following link:
S5-110U User Manual (English)You can also search for it on Siemens Industry Online Support using the article ID 10975807.
Given the age of the system, a full migration to a modern PLC (S7-1200/1500) is highly recommended.
Disclaimer: Program extraction without a backup carries risks. Professional assistance is advised.
Sincerely,
Siemens Self Support
It sounds like the 2nd CPU is failing to synchronize properly after the program reload and initial restart. Here's a breakdown of troubleshooting steps and answers to your questions:
While technically possible in some cases, it's strongly discouraged after a program error that caused both CPUs to stop. A clean synchronization with both in STOP is the recommended practice.
Dear Customer,
You are correct; the CP1413 card is limited by its driver support for Windows NT. Migrating to Windows XP with PCI slots necessitates a communication solution compatible with the new OS and interface.
CP 1613/1613-C is a suitable recommendation. It supports both PROFIBUS and MPI/PPI communication for your S5 PLC (Sinec H1) and has drivers available for Windows XP.
Further Considerations:
Since you're also migrating the S7 PLC, ensure the new S7 supports communication via the chosen CP card.
Sincerely,
Siemens Self Support
Dear Customer,
Siemens Self Support understands you're looking for information on modifying text and messages within your COMGRAPH project for the CP 528 visualization of your chocolate machine.
Unfortunately, direct documentation for COMGRAPH programming specifically for the CP 528 is limited. However, the core principles remain consistent with other COMGRAPH applications.
Modifying Text in Pictures: Within a full graphic window, you've already identified the correct approach – directly edit the text within the object properties. Ensure you save the changes to the graphic object.
Changing Messages: Message modifications are typically handled within the COMGRAPH configuration. Look for the "Messages" or "Text Libraries" section in COMGRAPH. You can define and edit message IDs there, which are then referenced within your application logic.
Further Support Resources:
If you continue to experience difficulties, please provide more details about the specific message you are trying to modify.
Sincerely,
Siemens Self Support
Hello! Converting S5 files to S7 often involves understanding specific function blocks (FBs) like FB1 (ADD:32) you've encountered.
Detailed descriptions of these standard FBs (and their S7 equivalents) can be found in the Siemens documentation. Here are some helpful resources:
For ADD:32 specifically (likely an addition instruction), look for details on the ADD instruction within the S7 instruction set. It has likely been converted to a standard S7 ADD instruction.
Hello, I understand you need a wiring diagram for connecting a 6ES5511-5AA12 AS511 card (25-pin) to a 15-pin PC-TTY interface, and you're facing issues with your SINUMERIK 3 after a power failure.
Unfortunately, a direct, readily available wiring diagram for a 25-pin AS511 to a 15-pin PC-TTY is difficult to locate. The original Siemens adapter (likely a specific RS232 cable with appropriate pin assignments) is crucial.
I recommend searching the Siemens Industry Forum: Siemens Industry Forum. Specifically, look for posts related to "AS511", "6ES5511-5AA12", "SINUMERIK 3", and "PC-TTY interface". Users may have shared information on custom cable builds or adapter details.
The fact that your machine doesn't start automatically after reloading data, and the PLC modifications weren't saved to the EPROM, is significant. You'll need to re-enter or restore those PLC program modifications. Accessing the S5 program is key, which is why the adapter is critical.
Once you have connectivity via the adapter, you can use a Siemens programming software (STEP 5) to download/upload the PLC program.
Please also utilize SiePortal for additional documentation and support: SiePortal. Search for your specific SINUMERIK 3 model and AS511 card.
If you can provide the exact SINUMERIK 3 model number, I can attempt to locate more specific documentation.
The QVZ LED on the Siemens 155H CPU indicates a Zero Voltage Detection fault. This typically means the CPU is not receiving sufficient or stable 24V DC power.
Possible Causes:
Troubleshooting Steps:
For more detailed information, please refer to the following resources on SiePortal:
SiePortal Forum Discussion - QVZ LED Lit on CPU 155H Siemens Support - Fault diagnosis in SIMATIC S7-1500/1511/1516