Hey ,
I know that I have to adjust p8840 (fieldbus off-time) (any other suggestions are welcome on this error) but what does fault value 11 means ?
Where can I find this back ?
Best regards,
You've installed the GSD file for the Sinamics G120 but it's not appearing in your Step 7 hardware configuration, and instead you only see G130/G150. This is a common issue often related to the GSD file version or hardware support package.
Here's how to resolve it:
Important Note: If you're using a very old version of Step 7, consider upgrading to a more recent version for better compatibility and support.
For further assistance, please refer to Siemens documentation or create a support request via SiePortal: Siemens Support
Hello! As Siemens Self Support, integrated with SiePortal, I understand you're encountering issues with accessing all parameters in the BOP (Basic Operator Panel) of your Sinamics drive, specifically expert parameters like P2040 and P0700 related to PROFIBUS.
This is a common experience for new Sinamics users. Here's a breakdown of how to resolve this:
Expert parameters are intentionally hidden in the BOP by default to prevent accidental modification. You need to explicitly enable their visibility.
Follow these steps in the BOP:
Caution: Enabling expert parameters allows access to settings that, if changed incorrectly, can impact drive functionality or safety. Proceed with caution and consult relevant documentation.
After setting P1000 = 1, restart the drive (power cycle). The previously hidden parameters, including P2040 and P0700, should now be visible in the BOP under the corresponding parameter groups.
If you continue to experience issues, please provide your exact drive model (e.g., Sinamics S120, G120) and firmware version for more tailored assistance.
Hello! As Siemens Self Support, integrated with SiePortal, I can help you with your Sinamics G120 configuration.
For detailed parameter descriptions and configuration guidance, please refer to the Sinamics G120 documentation on SiePortal: Sinamics G120 Documentation.
You are experiencing limited Modbus RTU address access with your Sinamics G120 PM240 (PM240E-2, 6SL3244-0BB12-1BA1) using Macro 15.
The issue of only seeing addresses 40340-40349 and inability to write to 40100 (Start/Stop - 1150/1151) is likely due to parameter P0700 (Modbus access mode) being incorrectly configured.
For further assistance, please provide your complete parameter configuration (P0700-P0704) and a description of your Modbus master device.
Dear Guest,
Thank you for reaching out. We understand you're experiencing issues with multiple control units exhibiting a dim SF LED, traced to swollen/burst electrolytic capacitors. This is a known issue that can occur, especially in environments with high operating temperatures or voltage fluctuations.
Known Issue & Potential Causes:
Recommendations:
We are constantly collecting data on field issues. Your report helps us improve product reliability. Please report any further occurrences via SiePortal for tracking purposes.
Sincerely,
Siemens Self Support
The F3003 error typically indicates undervoltage. Receiving 380V with a 400V drive/motor setup can indeed trigger this fault.
Here's how to address this:
Important Resource: For detailed troubleshooting steps and parameter explanations, please refer to the Sinamics G120 Firmware Manual and the F3003 Fault Description in SiePortal.
If the problem persists, consider contacting Siemens Technical Support with your drive type and STARTER project file for further assistance.
Dear Customer,
You are correct to observe that the Sinamics G120 (CU240E-2 PN) can automatically extend the ramp-down time (P1121) even if it's above the minimum set in P1127. This behavior is by design and relates to braking power limitations, as you've noted in the documentation.
The drive prioritizes safe deceleration. If the calculated braking power based on your motor, load, and brake resistor is insufficient to decelerate within the set P1121 time, the drive automatically increases the ramp-down time to prevent overvoltage or other fault conditions.
Even if you believe you have the correct brake resistor, several factors can influence effective braking power:
Recommendations:
For detailed assistance, please consult the Sinamics G120 Firmware Manual, section on braking choppers and brake resistors.
Sincerely,
Siemens Self Support
Error F0350 ("Error configuring the vector for the drive") coupled with r0949 = 1 indicates an internal error related to the hardware configuration vector on your CU240E.
Important: Four-digit error codes like F0350 indicate a more serious issue than three-digit codes. Carefully follow the troubleshooting steps and document all findings before contacting support.
For further assistance, please open a support request via the Siemens Industry Online Support portal, referencing this error code and your hardware versions.
Fault value 11 in SINAMICS drives typically indicates a DC link undervoltage. This means the voltage on the DC link (the energy storage component) has dropped below a safe threshold.
While adjusting parameter P8840 (fieldbus off-time) can sometimes mitigate issues related to communication-induced voltage drops, it's crucial to address the root cause of the undervoltage.
Possible Causes & Suggestions:
Where to find more information:
You can find detailed information regarding fault values, troubleshooting steps, and parameter explanations in the following resources on the Siemens Industry Online Support portal (SiePortal):
Please consult the documentation specific to your SINAMICS drive model for the most accurate information.
Yes, it is possible to control a G120 drive (with CU240b-2DP) from the terminal and simultaneously read parameters via PROFIBUS. The drive supports both modes of operation concurrently.
However, be mindful of potential conflicts if both interfaces attempt to write to the same parameters simultaneously. Typically, reading via PROFIBUS won't interfere with terminal control, but simultaneous writes might require careful consideration of priority and timing.
Relevant Documentation:
Important Note: Ensure your PROFIBUS configuration is correct (e.g., correct node address, baud rate) and that the drive is properly integrated into the PROFIBUS network before attempting simultaneous operation.