Dear all,
after 15 consecutive days of working with Scout TIA V13 Sp1 I am really annoyed about some things, but one of them is surely the online "path".
This is what happens.
I switch on my pc (the previous day I worked with it with same project, same machine) and connect to the machine (example: Simotion).
In Scout appears an "error" that says that it cannot reach the device.
So I go back to TIA and click "go online", I select the card, and everything, I do the "search" button, it finds me the Simotion, I click connect, then after it's connected, I click on Disconnect.
I go to Scout and it can connect with no problems.
So I can work.
After, I disconnect from Simotion, but leave the Scout opened in background. I go to WinCCV13 and click on "download software".
Again the same crap: it asks me to select the network card, then to browse for accessible devices, etc.
Ok I do that, download my HMI project. And it's "fine".
Now I go back to Scout and .... GRRRRR
It cannot go online, need to do the procedure again on TIA, like I previously said.
It seems that alternating downloads to Simotion, then to WinCC V13 (Basic Panel) forces me everytime to redo the connecting "procedure".
And this is an enormous loss of time everyday.
I have put the "favourite" path in TIA, but this doesn't help me at all.
What can I do ? In the old Scout/Wincc2008 this didn't happen...
It's like that TIA has the alzheimer , because it forgets everything about the online access method...
The error 40008 during cam generation, specifically with offset issues on the D445-1 V4.3 controller (while working on D425-2 V5.1), coupled with LCamHdl error 400C/21, strongly suggests a configuration mismatch related to interpolation and offset handling.
Possible Causes & Solutions:
SiePortal Resources:
If these steps don't resolve the issue, please provide the cam profile configuration and a sample program for detailed analysis.
You've correctly identified the limitation with using a positive-only force limit when employing differential force measurement for bidirectional hydromotor control. The _enableforcelimitingvalue function inherently works with positive values, causing issues when the differential force becomes negative during reverse operation.
Here's how to address this:
abs(differential_force) and applying the limit to the absolute value). However, ensure this doesn't negatively impact control responsiveness.Important Resources:
_enableforcelimitingvalue function and related force control parameters within your specific controller (e.g., SINUMERIK, SIMATIC). SiePortal is a good resource: SiePortalIf you can provide the specific controller you are using (e.g., SINUMERIK 840D sl, SIMATIC S7-1500), I can provide more tailored guidance.
The error message "With Silent Installations, the SetupMode.ini file must be copied into another directory and changed" indicates an issue with your installation method. This typically occurs when attempting a silent installation without proper configuration.
Resolution:
SetupMode.ini file from the Scout V5.5 installation source to a different directory.SetupMode.ini file to configure your silent installation parameters.SetupMode.ini.For detailed instructions and available parameters, please refer to the Siemens documentation on silent installations for Scout:
Siemens Support Article - Silent Installation ScoutIf the problem persists, consult the Scout V5.5 documentation or open a support request via SiePortal.
You're encountering difficulties downloading Scout projects and WinCC screens through a VPN due to NAT and IP address conflicts. Here's a breakdown of the issue and potential solutions:
The core problem is that Scout and WinCC are configured with the VPN's IP address (10.9.50.100/10.9.50.101) after you reconfigured the Simotion IP within NetPro. This causes hardware configuration download failures because the hardware configuration itself now references the VPN IP, which is unreachable once the VPN connection shifts or terminates.
route 10.9.50.0 mask 255.255.255.0 100.100.100.111) is a good start, but verify the customer site's VPN device is properly translating 10.9.50.x to 100.100.100.x.Disclaimer: Incorrect network configuration can disrupt operations. Proceed with caution and ensure you have a backup before making any changes.
Dear User,
Migrating a Simotion D410 program to a D425 while preserving the existing program logic generally involves these steps:
For detailed guidance, please refer to the Siemens Support article and FAQ's on SiePortal: Simotion D425 Migration. Also, review the Simotion documentation for specific hardware differences between D410 and D425.
If you encounter specific errors or have further questions, please provide details about the error messages or issues you are facing.
Sincerely,
Siemens Self Support
Based on the symptoms (all LEDs blinking red, no communication, error code F) and troubleshooting steps taken, the Simotion CPU likely experienced a critical failure.
Inserting the old CF-card into the new CPU may work, but it's not guaranteed. It depends on whether the firmware and configuration on the old card are compatible with the new CPU's hardware. Given the complete failure you experienced, it’s risky.
Since the customer provided the CPU reference number to Siemens, the replacement should be the correct version. However, it's prudent to confirm with Siemens if the delivered CPU is identical in hardware revision. A hardware revision change could necessitate a firmware update or configuration adjustments. Check the article Simotion CPU - How to determine the hardware and firmware version for more details.
Copying the old content to the new CF-card is not recommended without verifying compatibility. The new CF-card might require a specific firmware version or configuration for optimal performance and stability. Use the Siemens tools to configure the new card.
The multiaxis license is typically tied to the CF-card. Contact Siemens support to transfer the license to the new CF-card or the new CPU. Do not attempt to simply copy the license file; this often results in an invalid license. See How do I transfer a license to another hardware? for guidance.
Recommendation: After receiving the new CPU and CF-card, use Siemens tools (e.g., SCOUT) to properly configure the system and apply the necessary licenses. Contact Siemens support for assistance if needed.
Implementing a hardware emergency stop is critical for safety. It's strongly recommended to utilize dedicated safety inputs on your motor starter/drive and safety PLC (e.g., SIMATIC Safety Integrated) rather than relying solely on pulse enable inputs on the motor module.
A dedicated safety circuit provides the highest level of reliability. This involves:
While you *can* use a pulse enable input, it's not a safety-rated solution. It relies on the PLC continuously sending a pulse, and a PLC failure could prevent the pulse, leading to uncontrolled motion. It can be used as *additional* safety layer with a safety circuit.
Disclaimer: Safety implementations are application-specific. Consult safety standards (e.g., ISO 13849, IEC 61508) and qualified safety engineers to ensure a safe and compliant design.
The error you're encountering after adding a boolean array to your variable structure likely stems from a size limitation or data type conflict within the proxy data handling in TIA Portal.
Possible Causes & Solutions:
Further Investigation:
Please review the TIA Portal documentation regarding proxy data limitations and data type compatibility. You can find helpful resources on the Siemens Industry Online Support. If the issue persists, provide the exact error message and details about the array size for more specific assistance.
Establishing distributed synchronization between Classic Scout and Scout TIA projects using DP communication requires careful configuration on both sides. Here's a breakdown of the key steps and troubleshooting points:
If issues persist, consider opening a support request through the Siemens Industry Online Support portal, providing detailed project information and error logs for faster resolution.
Dear Sandip,
You can upload and download parameters to/from your MicroMaster 440 inverter using SIMOTION Scout. Here's a guide:
Important Resources:
Refer to the MicroMaster 440 hardware and SIMOTION Scout documentation for detailed instructions and troubleshooting.
Sincerely,
Siemens Self Support
Dear Customer,
It appears the Control Unit (CU305 DP) is not recognizing the new driver PCB (A5E03894525) on your PM340 power module after replacement. This typically requires parameter re-initialization.
Here's a troubleshooting approach:
If the issue persists, please provide the following information for further assistance:
You can find additional resources and FAQs on the Siemens Industry Online Support.
Sincerely,
Siemens Self Support
Hello Szymon,
I understand you're facing issues establishing a Profibus connection between your Simotion D435 and Simatic S7-315-2DP, with the S7 as master and Simotion as slave. The Simotion station appears active in the PG/PC interface, but isn't visible in the Simatic HW configuration.
Here are potential causes and troubleshooting steps:
For a detailed guide and example, refer to this FAQ: Profibus DP communication between SIMOTION and SIMATIC S7.
If the problem persists, please provide the following information for further assistance:
Best regards,
Siemens Self Support
Dear Customer,
The error "PEData.plf' could not be upgraded" during a Simotion backup upgrade from V13 to V14 typically indicates an incompatibility or corruption issue with the PEData file. Simply copying the file isn't always sufficient.
Here's a breakdown of potential causes and solutions:
Further Support:
Please refer to the Siemens Support article PEData.plf Upgrade Issues for detailed troubleshooting steps.
If the issue persists, please create a support request on SiePortal with the error screenshot and project details for expert assistance: SiePortal
Sincerely,
Siemens Self Support
Dear Sam,
Yes, you can install Scout alongside your existing Siemens software (Step 7, TIA Portal versions 13-15). However, the error message indicates a missing dependency.
1. Compatibility: Scout 4.4.0.11 requires SIMATIC S7 F Configuration Pack V5.5.11.0 or higher to be installed. This is a known prerequisite.
2. Download Location: You can download the SIMATIC S7 F Configuration Pack V5.5.11.0 (or a newer version) from the Siemens Support website via SiePortal:
SIMATIC S7 F Configuration Pack V5.5.11.0 DownloadAfter installing the Configuration Pack, you should be able to install and run Scout 4.4.0.11 without issues.
If you continue to experience problems, please provide more details about your operating system and specific TIA Portal installation configurations.
Sincerely,
Siemens Self Support
You're encountering a common issue when interfacing SINAMICS drives (CU320) with SIMOTION D445 via PROFIBUS, specifically concerning data type mismatches and resulting timeout errors.
Here's a breakdown and troubleshooting steps:
Resources:
If the problem persists, provide your exact SIMOTION and SINAMICS firmware versions, and a screenshot of your PROFIBUS address list configuration. Also confirm the exact PZD2 configuration.
Dear MNA,
Based on your description, the issue appears to be related to communication or data inconsistencies between the S7-400 PLC and the Simotion D435 after switching between MDS units. The discrepancy between the PLC-sent setpoint and the value received by Simotion (r2060[1]) is a key indicator.
Here are potential causes and troubleshooting steps:
Further Investigation:
Access SiePortal and search for similar issues related to "Simotion setpoint mismatch" or "Simotion MDS changeover". You might find relevant FAQs, knowledge base articles, or forum discussions.
If the problem persists, consider opening a support request through Siemens Support with detailed logs from both Simotion and the PLC.
Sincerely,
Siemens Self Support
Dear Customer,
You can reuse your existing MMC card (6UA1700-0AA02-0AA0) from the Simotion C230-2 with the new Simotion C240. However, a few steps are necessary to ensure compatibility and proper functionality:
For detailed guidance and specific instructions, please refer to the following resources in SiePortal:
If you encounter any issues, please don't hesitate to create a support request in SiePortal with detailed information about the problem.
Sincerely,
Siemens Self Support
Dear User,
We understand you're facing issues with an ascending order program in Simotion D425-2 DP/PN simulation, while it functions correctly in S7-1500 simulation. This discrepancy often arises from differences in hardware-specific instruction behavior and cycle times.
Possible Causes & Troubleshooting:
Sample Program & Resources:
You can find relevant examples and documentation on the Siemens Industry Online Support: Siemens Industry Online Support. Search for "Simotion ascending order example" or "Simotion sorting example". Also, explore the SiePortal for Simotion specific FAQs and knowledge base articles: SiePortal.
If the problem persists, please share the program code (or a simplified, representative section) and the Simotion hardware configuration for further analysis.
Sincerely,
Siemens Self Support
The issue you're experiencing with the Simotion D425-2DP system, where the SAM1(2) drive crashes into the fence at higher production rates (2500 trays/hour), suggests a potential problem with the drive's ability to accurately control position during rapid acceleration/deceleration cycles.
Here's a breakdown of potential causes and troubleshooting steps, leveraging Siemens resources:
Important: Due to the potential for damage and safety concerns, carefully test any parameter changes in a controlled environment before returning the system to full production.
You're encountering an error because your Simotion Scout V4.1.5.15 (version 47.80.30.00) is attempting to open a project created with a newer version (62.28.00.00) of the S120 drive firmware/Scout software.
Solution: You must update your Simotion Scout software to a version equal to or newer than the version used to create the backup.
Recommended Update: Download and install the latest Simotion Scout V4.1.5.15 Update from the Siemens Support Portal. Ensure you have the correct update for your specific hardware and software configuration. Check the release notes to confirm compatibility with S120.
Important Note: Always back up your current Scout installation before applying any updates. Refer to the SiePortal documentation for detailed upgrade instructions.