HEY,
I would like to use the new CPU 314C PN/DP (6ES7 314-6EH04-0AB0) in one application.
But I noticed, that it can be programmed by STEP7 V5.5 or higher with HSP191 !!!!!!! But I have S7 V5.4 SP5 !!!! (see the enclosure)
- Do you think, I can use my S7 V5.4 for this module ?
- How to upgrade to version 5.5 ?
- Is it free ?
- And what is HSP191? HW catalog update ?
Thank you very much for your answers !!!!!
Jiri Matus.
Dear Nanu,
To change the actual axis value configured through FM357-2 and write parameters from the PLC, you'll primarily utilize the FM357-2's parameter interface via PROFIdrive/PROFIsafe.
Changing Actual Axis Value: You can modify the actual position value by writing to the Position Demand Value parameter (parameter number varies based on drive configuration – check your hardware configuration list - HCL). This is typically done using the 'Write Parameter' function block in your PLC program, communicating through PROFIdrive.
Writing Parameters (PRESET Function): To configure the PRESET function via PLC:
Important Resources:
For detailed step-by-step instructions and troubleshooting, consult the FM357-2 documentation on SiePortal and consider searching for application examples related to PLC-based parameterization.
Sincerely,
Siemens Self Support
Good day! It sounds like you're experiencing a recurring issue with a module, despite replacement. Since you've already verified input signals, let's explore potential causes.
To assist you further, please provide the following information via Siemens Support Portal :
We can then leverage SiePortal's knowledge base and expert resources to pinpoint the root cause.
It sounds like you're experiencing intermittent loss of retained data from your CPU 315-2DP (6ES7 315-2AH14-0AB00) despite using non-retain DB settings. The fact that a firmware upgrade to 3.3.8 seems to have resolved it is a positive sign, but the rarity of the issue makes confirmation difficult.
The CPU 315-2DP uses the MMC card to store retained data (DBs) during power loss. The process involves:
Your suspicion about the 3rd-party power supply is valid. Here's a breakdown:
No, it is generally not possible to directly send programs from WinCC Flexible (WinCC Flex) to an OP77A HMI via Ethernet when using a CPU 313C with an MPI/PROFIBUS interface and a CP343-1 Lean for programming.
Here's why:
Recommended Approach:
For more information, please refer to these resources on the Siemens Support website (SiePortal):
If you have a specific network configuration and are attempting a different approach, please provide more details for a more accurate assessment.
The successor to the 1XP88001-1/1024 PULSE ENCODER is the 6ES7193-0CA00-0AA0.
Please refer to the SiePortal for detailed information, including specifications and ordering information: Siemens Support Link.
You may also find helpful information regarding migration and compatibility on the Siemens Industry Online Support platform.
Yes, it is possible to connect a reference point switch and hardware limit switches to the FM 353 for stepper motor control. The FM 353 provides sufficient inputs for this purpose.
Within your STEP 7 project, you'll need to configure the FM 353's input modules and associate the DI addresses with the relevant functions in your technology object (PTO/PTP). Specifically, map the DI's to:
Refer to the FM 353 manual (available on Siemens Support) for detailed wiring diagrams and configuration instructions. Also, review Siemens documentation on PTO/PTP objects for configuring stepper motor control and limit switch integration.
You've encountered a common issue related to grounding and potential differences when wiring analog modules. The behavior you observed (all channels reading 7FFF) indicates a ground loop or potential difference issue.
While a single definitive guide doesn't explicitly detail this specific scenario, Siemens documentation addresses key principles. Here's a breakdown and relevant resources:
Recommended Resources:
Troubleshooting Tip: Always verify the ground potential between the signal source and the module before connecting. A multimeter can help identify unwanted voltage differences.
Dear Vorapob,
You can backup the project file from the MC card of your S7-317F CPU to another MC card using a PC adapter designed for MC cards. Here’s how:
For detailed instructions and compatible hardware, please refer to the following resources on SiePortal:
Best Regards,
Siemens Self Support
Hello, as Siemens Self Support integrated with SiePortal, I can assist you with locating sales options and addressing your Industry Mall registration issue.
Since you don't have local distributors in Albania, here are options for purchasing directly:
Registration problems can occur due to several reasons. Please try these steps:
I hope this helps! Don't hesitate to ask if you have further questions.
Dear Customer,
We understand you are experiencing issues with configuring the integrated analog inputs/outputs (AI4/AO1) on your SIMATIC 314 IFM CPU (6ES7-314-5AE03-0AB0) within Step 7 V5.5 SP4 HF11.
This behavior – where the analog modules are visible with a CPU 313C but not the 314 IFM – is a known issue related to the hardware configuration data within the Step 7 project. The CPU 314 IFM requires specific hardware support data that might be missing or corrupted in your current project.
If the issue persists, please provide your Step 7 project (or a simplified version demonstrating the problem) to Siemens Support through the SiePortal for further investigation. Please include screenshots of your HW Config showing the missing modules.
Sincerely,
Siemens Self Support
You are correct to notice the limited Function Card (FC) options for the AI 465 with measure module 498-1AA41. Currently, Siemens documentation primarily lists FC 460, 463, 464, and 466 as compatible.
Regarding using FC 100 instead of the older FC 350: FC 100 is generally not a direct replacement for FC 350. They have different capabilities and may not support all the features required by your AI 465/498-1AA41 configuration.
Recommendation: Please consult the Siemens Support or review the SiePortal documentation specifically for the AI 465 and 498-1AA41 module to confirm compatibility. Providing your specific application details to Siemens Support will help determine the best FC option.
Dear Ganesan,
You are correct, Siemens does not offer a dedicated failsafe analog output module like those available for digital outputs.
Achieving failsafe behavior with analog outputs is significantly more complex due to the continuous nature of the signal. Detecting a 'safe' state requires more sophisticated diagnostics and considerations for signal degradation.
For detailed information and support articles, please refer to the SiePortal:
Siemens Industry Support PortalSincerely,
Siemens Self Support
You're experiencing issues changing I/O addresses on your S7-300 hardware. This typically occurs due to configuration errors or hardware restrictions.
Here's a breakdown of potential causes and solutions:
For detailed troubleshooting steps and FAQs, please refer to this SiePortal FAQ on Changing I/O Module Addresses.
If the problem persists, please provide more details about your setup (STEP 7 version, CPU type, specific modules affected) for further assistance. You can also search for specific error messages in the Siemens Support Portal.
Dear Paresh,
Here's a breakdown of register details for S7-300 PLCs, specifically for CPU 314 and CPU 315-2 DP, along with information on cycle performance. Please refer to the Siemens documentation linked below for complete details.
The number of registers you can read or write in one cycle depends heavily on the program complexity, instruction mix, communication overhead, and hardware configuration. However, as a general guideline:
Important Note: The maximum achievable performance should be determined through testing and profiling your specific application.
For detailed information, please consult the following Siemens documentation:
Sincerely,
Siemens Self Support
Integrated with SiePortal
Based on your detailed description and troubleshooting steps, the issue appears to be related to a hardware fault specifically triggered by the wiring or the IM 151-1 HF module itself, rather than a software configuration problem.
If the above steps don't resolve the issue, consider opening a support request with Siemens directly via the Siemens Support Portal. Be sure to include the diagnostic buffers and a detailed description of all troubleshooting steps taken.
Yes, it is generally possible to temporarily connect an analog output (AO) channel directly to an analog input (AI) channel for testing purposes, but with caution.
Since you're troubleshooting a loop-powered 4-20mA positioner, verifying the AO signal is a good first step. Connecting to an AI channel allows you to confirm the AO module is generating the expected 4-20mA signal range when commanded different output values.
Important Considerations:
For detailed information on Siemens AI/AO modules and configuration, please refer to the SiePortal documentation: Siemens Support Portal.
If the AO doesn't show correct values on the AI, investigate the AO module’s configuration and power supply. If the AO *does* function correctly, the issue likely lies with the Samson positioner or the wiring to it.
Dear SexDriver,
Thank you for your query regarding the IM153-2BA01 slave switching behavior in your redundant MySWR configuration (two 315-2DP-2AG10 CPUs with two IM153-2BA01 slaves, MPI redundancy).
The behavior you're observing – requiring an Overall Reset for the IM153-2BA01 to switch after initially downloading the hardware configuration – is a known issue. This is often related to initial state inconsistencies during the first switchover.
Key Considerations & Troubleshooting:
While an Overall Reset resolves the issue, it's not a sustainable long-term solution. Investigate the points above to address the underlying cause. If the problem persists, please open a support request via SiePortal (https://support.industry.siemens.com/) providing the diagnostic data for further analysis.
Best Regards,
Siemens Self Support
Based on the error messages and your setup, you're encountering a memory issue despite using a 256KB memory card. Here's a breakdown and solution:
The PLC 314 has limitations regarding memory card size and how it's utilized. The error "possible load memory bottleneck" indicates that the available memory (48832 bytes) is insufficient for the 100KB program, even though the card is larger. This is likely due to how the PLC addresses and manages memory, especially with the older CPU firmware.
Note: Always back up your existing program before making any changes.
You are correct, this module supports both analog drives and stepper motors. When referring to "analog drives" in the Siemens context, we generally mean drives that accept analog input signals (typically 0-10V, -10 to +10V, or 4-20mA) for speed or torque control.
Here are some Siemens drive series considered analog drives that can be connected:
Important Note: Always consult the drive's documentation and the module's manual to ensure compatibility and proper configuration regarding voltage/current ranges and signal scaling.
For detailed compatibility information and specific configuration instructions, please refer to the Siemens Industry Online Support and search using your module's article number.
Based on your description (SF LED on, RUN LED on, +5V LED on, OB80/85/121 not loaded, CPU stuck), and the fact that the system *appears* to be running normally despite this, the issue likely points to a configuration inconsistency or a problem with the startup sequence.
The SF LED indicates a fault, but the lack of diagnostic messages is unusual. Here's a breakdown of potential causes and troubleshooting steps:
Important Note: Since all nodes are accessible, the PROFIBUS communication seems functional at a basic level. However, incorrect parameters can still cause internal CPU issues.
If these steps don't resolve the issue, please open a Siemens Support Request with the attached diagnostic buffer and your project backup for further analysis.