Hallo all,
First of all I would like to wish to all the users of the Siemens Technical Forum a great 2014, full of the technical riddles that will keep you all busy with Industrial Automation.
About the riddles, I have one.
I visualize the work of three pumps in the form of Trend View. Different color of the trend line for each pomp.
When the pomp is running, the value of the tag assigned to the trend changes so that I obtain something like the waveforms: for instance pump A stopped – tag value =0, pump A running – tag value = 20.
My goal is to save the trend even when the panel (TP1200 Comfort) is switched off. When the power goes down, the trend starts from the moment of the start. In other words, historical data is lost.
How to keep it? Is there any easy way to do it? Perhaps it is possible with “Historical data”? In the meantimeI will check out the "Historical data" and try to figure it out.
If the trend is not possible to save, is it possible with the data in the form of a table or list?
Thanks in advance for any help in this matter.
===================================================================
A little update: in the manual "WinCC Professional V12 - System Manual"I havefound following, promissing sentence:
"Outputting logged data; In runtime, you can output the logged tag values as trends in the process screens"
So the answermust beinData loggingand Trends, but how to do it?
Dear User,
Based on the screenshots, the issue appears to be related to communication problems preventing the factory reset or OS update of your HMI. Here are potential solutions:
If the problem persists, please provide the exact HMI model number and the specific error message displayed during the reset/update attempt. You can also open a support request via SiePortal for dedicated assistance.
Sincerely,
Siemens Self Support
Dear Iyyappan,
Migrating alarm annunciation from WinCC 7 to WinCC V11 requires careful consideration. Here's a suggested approach:
Resources:
For specific implementation details and troubleshooting, consult the WinCC V11 documentation and Siemens support forums. Please provide specific details of your existing WinCC 7 implementation if further assistance is required.
Sincerely,
Siemens Self Support
Based on the provided information, the SSL handshake failure with Sm@rtClient specifically from a VM on the 'public' network, while local and IPC access works, points to a client-side certificate issue. Here's a breakdown and potential solutions:
The issue is unlikely to be resolved by deleting or refreshing a single file. Focus on the certificate trust chain and SSL/TLS configuration.
For detailed instructions on updating certificates and configuring Sm@rtClient, please refer to these resources on SiePortal:
If the problem persists, consider opening a support request with Siemens Support, providing the HMI's certificate and detailed logs from both the HMI and Sm@rtClient.
You're experiencing a common issue: runtime recipe modifications are lost when the HMI stops. WinCC TIA Portal recipes, by default, don't automatically persist changes made during runtime unless configured to do so.
Here's how to achieve data persistence for offline use:
Important SiePortal Resources:
Review Siemens documentation and the provided links for detailed configuration steps specific to your WinCC TIA Portal version (13.0 SP1).
Hello, thank you for reaching out to Siemens Self Support. We understand you're experiencing a visualization error when adding gauges to your HMI/PC station project in TIA Portal V15.1.
This issue is often related to missing or corrupted graphic libraries. Here's a potential solution:
For further assistance and to review similar cases, please refer to this FAQ on the Siemens Support website: TIA Portal V15.1 Visualization Errors
If the problem persists, please open a support request through SiePortal, including the project (or a representative sample) and the error message details.
For reading a large number of tags (especially Booleans) from Siemens PLCs (1500/1200) over Industrial Ethernet (IE) with minimal communication load, avoid reading tags individually. Packing data is significantly more efficient.
Here's a breakdown of recommended approaches:
Why this matters: Each tag read creates a separate communication request (PDU). More PDUs = higher network load & increased PLC cycle time. Reducing the number of PDUs is crucial for performance, particularly with a large number of tags and multiple PLCs.
Further Information: Refer to the SiePortal for detailed guidance on optimizing communication with Siemens PLCs. Siemens Support Article and Optimize Communication
Hello masmith1553,
You've encountered a common challenge with screen adaptation in WinCC Professional V15.1. The 'Adapt screen' feature is designed to scale *down* to smaller resolutions, but reliably scaling *up* to larger resolutions, especially with aspect ratio changes like 4:3 to 16:9, can be problematic.
Here's a breakdown of the issue and potential solutions:
Important Note: WinCC's screen adaptation isn't a perfect solution for significant aspect ratio changes. Some manual adjustments to graphic sizes and positions may still be necessary.
For further detailed information, please refer to the Siemens Support article: Screen adaptation in WinCC (TIA Portal) does not work as expected
If you continue to experience issues, please provide screenshots of your screen properties and a sample project (if possible) through the Siemens Support Portal for further assistance.
Regards,
Siemens Self Support
You are correct that the UpdateTag function is documented for WinCC RT Advanced. The "Variable 'UpdateTag' is not defined" error typically occurs due to a namespace issue.
The UpdateTag function resides within the CIMRuntime namespace. To resolve the compilation error, you must explicitly qualify the function call with this namespace.
Correct Usage: CIMRuntime.UpdateTag(TagHandle, Value)
Please refer to the following SiePortal knowledge article for more details and examples:
Using UpdateTag function in WinCC RT AdvancedThis article provides a comprehensive explanation and troubleshooting steps. Updating tags on demand using UpdateTag is a valid approach to avoid unnecessary cyclic updates.
You are correct regarding the Runtime license: 6AV2105-3HH06-0AE0 (SIMATIC WinCC RT Professional, 4096 PowerTags V16, upgrade V11..V15 -> V16) is required for the core upgrade.
Regarding Web Navigator, the licensing is included within the WinCC RT Professional license. The upgrade license you've identified includes the necessary Web Navigator rights for up to 5 clients. No separate license is needed for the Web Navigator itself when upgrading within the same number of clients.
For detailed information on WinCC V16 licensing and compatibility, please refer to the official Siemens documentation on SiePortal.
Siemens Self Support
Hello! To connect another OPC server to WinCC TIA Portal, you'll primarily use OPC UA or OPC Classic connectivity. Here's a breakdown:
TIA Portal V17 and higher have native OPC UA support.
Refer to Siemens Support article for detailed instructions.
For older OPC servers, you might need the OPC Classic interface. This often requires a redistributable and configuration within WinCC Runtime.
See this Siemens FAQ for more information on OPC Classic.
Important: Ensure the OPC server is running and accessible from the TIA Portal engineering PC.
Here's a breakdown of limitations for WINCC Runtime Advanced V13, along with links to relevant documentation:
The maximum number of screens is largely dependent on the hardware and system configuration. However, a practical limit generally falls around 500-1000 screens for optimal performance. Excessive screens can impact loading times and runtime responsiveness.
The number of objects (buttons, fields, pictures, etc.) per screen is also system-dependent. A good practice is to keep the object count below 200-300 for complex screens to maintain performance. Simple screens can handle more.
The number of tags directly bound to a screen impacts performance. Aim for 50-100 actively updating tags per screen. Excessive tag connections can lead to slower update rates.
For detailed limitations and best practices, please refer to the official Siemens documentation:
WINCC Runtime Advanced System Documentation WINCC V13 - Configuration - ManualsThese links provide comprehensive details on system requirements, limitations, and configuration guidelines.
Hello! As Siemens Self Support, integrated with SiePortal, I understand you're facing challenges selecting recipes and data records from the PLC using the job mailbox. It's common to encounter initial hurdles when setting up recipe handling.
Jobs 69 & 70 are typically used for recipe transfer, but updating the HMI dropdown requires additional steps. The data record changes you observed indicate successful mailbox processing, but a separate mechanism triggers the HMI update.
Here's what you might be missing:
Resources:
For detailed configuration guidance tailored to your specific HMI and PLC, please provide the following information: HMI type (e.g., WinCC, TP series), PLC type (e.g., S7-1200, S7-1500), and the method you're using to link the recipe data to the HMI display.
Hello,
You are correct that Miniweb login credentials are typically configured directly on the HMI via WinCC Internet Settings. Unfortunately, TIA Portal v15.1 does not allow creating these credentials remotely.
Here are your options to access the alarm log file and Miniweb:
Important Note: For security reasons, avoid using default or easily guessable passwords.
For further assistance, please refer to the Siemens Industry Online Support and search for "TP700 Miniweb password" or "TP700 Alarm Log Access".
Best regards,
Siemens Self Support
The errors you are encountering ("undefined identifier 'TriggerOperatorEvent'" and "'TriggerOperatorEvent' is not a function") in WebNavigator after creating Operator Event logging scripts with a Release button event are a known issue in TIA Portal V16 Update 5 when using faceplates.
Cause: The TriggerOperatorEvent function is not fully supported or correctly interpreted in the WebNavigator environment despite functioning correctly in the client runtime.
Solution/Workaround:
TriggerOperatorEvent function specifically within scripts that are executed by WebNavigator. Consider alternative methods for triggering events or updating the HMI based on your requirements. For example, you might use indirect triggering through PLC variables.Further Information: You can find related discussions and potential solutions on the Siemens Support forum: Siemens Support Forum. Searching for "TriggerOperatorEvent WebNavigator" will likely yield relevant results.
Disclaimer: As Siemens Self Support, I am an AI assistant. For critical applications, always consult official Siemens documentation and support channels.
Hello! You can implement password protection for navigating between views in WinCC Professional V13 using User Management and appropriate scripting.
Here's a general approach:
Refer to the following resources for detailed guidance:
For TP900 panels, ensure the user management configuration is correctly deployed to the HMI device.
This error message, "No configuration file was specified on the command line or in the “HmiRTm.ini” file," typically occurs during runtime of a WinCC Runtime Advanced project.
Possible Causes & Solutions:
Further Support:
Please refer to SiePortal for detailed information and troubleshooting steps:
Siemens Industry Support PortalAlso check FAQ: How to start WinCC Runtime Advanced in command line mode.
Yes, it is absolutely possible to read and write Data Block (DB) variables from your KTP1000 Basic PN HMI with a S7-1200 CPU and TIA Portal V10.5.
For detailed step-by-step instructions and examples, please refer to these resources:
Siemens Self Support - Your partner for efficient solutions.
This issue, where objects vanish after closing a pop-up screen and reappear when another pop-up is closed, is often related to screen updates and object visibility management within WinCC (TIA Portal). The linked topic highlights this behavior.
Solution: You need to adjust the "Redraw" settings for the main screen. Specifically, ensure the screen is configured to redraw completely when regaining focus.
Explanation: When a pop-up closes, the main screen doesn't always update correctly without being explicitly redrawn. This can lead to objects becoming invisible. Forcing a complete redraw ensures all elements are refreshed and displayed properly.
For more detailed information and examples, please refer to the following Siemens Support article:
Objects disappear when picture pop up in WinCC 7.3 runtimeHello! I understand you're following the YouTube tutorial (https://www.youtube.com/watch?v=AJYzyGMSg7w) and having trouble stopping the moving object, even with a PLC timer.
Directly stopping a moving object via a PLC timer isn't the typical approach in WinCC Basic. The animation path needs to be controlled. Here's what commonly works:
For detailed information and examples, please refer to these resources on SiePortal:
If you continue to experience issues, please provide details about your PLC code (timer configuration and tag used), and the WinCC Basic animation settings (specifically, which property you are trying to control).
You're asking about similarities to WinCC V7 features in WinCC V11.
Yes, WinCC V11 supports structure tags similar to WinCC V7. You can define structures for both internal and external tags, allowing for organized data handling. The functionality is maintained and enhanced in V11.
The licensing for WebNavigator in WinCC V11 largely follows the V7 model. You'll require:
For detailed licensing information, please refer to the official Siemens documentation on SiePortal: SiePortal. Search for "WinCC V11 licensing" or "WebNavigator licensing".