Browse Questions » WinCC Unified Systems: "Dynamization does Not work if two Alternatively more From those bits come "true" Located At the Identical time" - is it true?

About User

Questions Asked: 24.4K

Answers Given: 0

0
  • Open

WinCC Unified Systems: "Dynamization does Not work if two Alternatively more From those bits come "true" Located At the Identical time" - is it true?

As from WinCC Unified V18 there is the option off dynamisation with multiple bits.
BUT!
Apparently the dynamization does NOT work if two or more of those bits come "true" at the same time. For expressions, WinCC takes the first one that is satisfied, but that does not happen here.
Or am I wrong? 
I'm on WinCC Unified V18 Upd 2
------------------------------------------------------------------------------------------
Split from
WinCC Unified Faceplate multiple bits.
.

0 Likes 0 Favourites 0 Followers 0 Comments
Answers(1)

WinCC Unified V18 Dynamization with Multiple Bits

You are correct in observing that WinCC Unified V18 (Update 2) dynamization, when using multiple bits, does not evaluate all true conditions simultaneously. It prioritizes the first bit that evaluates to TRUE and applies the corresponding action. Subsequent TRUE bits are ignored for that specific dynamization instance.

This behavior is by design. If you require evaluation of multiple conditions, you'll need to use alternative approaches like combining the bits using logical OR operators within a script or expression linked to the dynamization trigger.

For further details and workarounds, please refer to the following resources on the Siemens Support website:

If you continue to experience issues, please open a support request via the Siemens Support Portal, referencing KB1000606293 and KB1000597787.